Cable VT or Busbar VT configuration

Cable VT or Busbar VT configuration

Cable VT or Busbar VT configuration

(OP)
I have a 6.6kV switchboard with 2 Incomer panels and a Bus section. Both incomers will be supplied from an islanded Diesel Generating station. How do I select the position of the VTs on each incomer, i.e. busbar or cable connected VT?
Thank you.
H

RE: Cable VT or Busbar VT configuration

It would depend a great deal on what you intend to do with the voltages as to where you should derive them.

RE: Cable VT or Busbar VT configuration

For instance:
If each incomer is connected with other D.G. then you need to put them in parallel. In this case you need
-at least-one VT on each incomer –before the breaker-and -at least- two VTs in V- on the bus bar[for measurement, too].

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources