Cable sizing for 600-1000 Vdc
|
RE: Cable sizing for 600-1000 Vdc
IEC 60287-1-1 CH.1.4.1.2 DC cables up to 5 KV
No dielectric losses involved, no skin effect, no proximity effect. Since wd=0 , skin effect and proximity
effect are 0 –the conductor resistance is less-and no shield, armor and conduit loses then the current will
be more elevated. The percent of permissible d.c.current increasing with respect to a.c.will be more
for elevated voltage[however up to 15 KV the dielectric losses are negligible] and large conductor cross section.
RE: Cable sizing for 600-1000 Vdc
Alan
“The engineer's first problem in any design situation is to discover what the problem really is.” Unk.