Is it common to install a diode in series with a 4-20mA circuit?
To prevent backfeeds on a 4-20mA circuit is it common to put a diode in the loop? I know there is a voltage drop across the diode, and the voltage being relatively small, I wonder if this is a good idea?
RE: Is it common to install a diode in series with a 4-20mA circuit?
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
> The destination is supposed to be a purely passive device, and there is no expectation that such a situation could occur
> The addition of protective circuitry has the potential of introducing additional noise. For the diode example, the rectification feature of the diode makes it likely that coupled noise winds up being rectified, resulting in a non-zero mean, resulting in additional noise that can no longer be filtered.
TTFN
So all the current through the diode will divert through the ammeter? What is the resistance of the diode?
I guess this for troubleshooting?
Keith Cress
Can you explain what that means...forward voltage? And perhaps the basics of an ammeter in a nutshell?
I'm not following how this works and why.
24vdc---+--[Diode]->+-->23.4V
-----AM------
An ammeter is nothing more than a resistor, (generally of very low value), that is observed by a voltmeter. Ohms law describes what the voltmeter will see given any specific current.
Keith Cress
TTFN
Diode resistance can be viewed as roughly the inverse of the diode current, so the parallel resistance of the diode will be at best 8ohms at 100mA, in the cited webpage, and if the current meter has a resistance of say 0.5ohm: http://www.fluke.com/fluke/usen/wireless-testers/d... then at 100mA, the voltage burden of the ammeter will only by 50mV, where the diode resistance is many kohms.
TTFN
Pretty much, with the exception that an ammeter has a burden and so has a finite voltage drop - not 0V.
Keith Cress