Current in power distrobution
2

Current in power distrobution

Current in power distrobution

(OP)
Hi guys,

Fairly new to electronics to you may have to bare with me!

I've recently started working as part of a stage crew where we deal with power on a day to day basic. We run 63 amps through a distro which outputs to 16A, 13A, 15A.....etc

What i cannot seem to get my head around is how the current it distributed

Take this product by Rubber Box http://www.rubberbox.co.uk/on-the-shelf/splitters/...

How can it have an inlet of 16A 240V and two outlets of 16A 240V?
Surely it would have to be 32A 240V inlet to 2 x 16A 240V outlets?

And the same goes for the 63 amp distros that we use that distribute more than 63 amp out

Please unconfuse me!

Thanks in advance
Chris

RE: Current in power distrobution

Just because it's rated for 16 amps does not mean that your going to use it. It's a standard sized connection (so they are all the same), the incoming could be 16 amps, and then one outgoing could pull 2 amps and the other 14. Most likely it would be around 10 amps and 3/7 amps for the outgoing. Equipment tends to be oversized so they don't fail during productions (the actors complain if they catch on fire).

RE: Current in power distrobution

If the panel is 63 Amps three phase, you have 63 Amps on each of three phases

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Current in power distrobution

It is actually difficult to follow your thinking. But I think that you mean that the two outputs shall carry rated current, say 16 A, and that you then need to input twice that sum - but that is not allowed.

If that is how you are thinking, then rethink. The total capacity is 16 A. Period. You can load output #1 with 16 A and zero from #2. Or you can use any combination of loads on #1 and #2 as long as the sum doesn't exceed 16 A. Capish?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Current in power distrobution

(OP)
Ahh right gotcha!

Thanks!

RE: Current in power distrobution

Fine! And welcome to Eng-Tips! Appreciate you using "civilized" writing instead of txt, which is getting on my nerves.

You say 240 V - is that UK? I thought you had 'harmonized' like the rest of Europe? You know, we went from 220 V to 230 V to meet you half-ways. Shouldn't you also go to 230 V, then? Or are you cheating on us? wink

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources