(OP)
Hi,

We have 11kv,250mva fault level given by utility.Then we have a
Transformer 11/0.415kv,%z-6% transformer.My question is what wll be Fault MVA
at 0.415kv.

thanks in advance

Abraham

RE: FAULT LEVEL

and MVA transformer??

RE: FAULT LEVEL

(OP)
Hi,

1500kva

thanks

RE: FAULT LEVEL

Network impedance:
Zn=11E3^2/250E6=0.484
Transformer impedance in per unit:
Ztpu=0.06
Impedance base on primary with Sbase of 1500kVA:
Zbn=11E3^2/1500E3=80.67
Network impedance in per unit:
Znpu=0.484/80.67=0.006
Total impedance in per unit:
Znpu+Ztpu=0.066
Fault current in per unit at 100% voltage:
Ifpu=1/(0.066)=15.15
Current base on secondary of transformer:
Ib=1500E3/(3^0.5*415)=2087
Actual fault current on secondary:
If=Ifpu*Ib=2087*15.15=31618 amps

RE: FAULT LEVEL

You might want to include a voltage factor in wroggents answer depending on what part of the world you are in. IEC60909 would need 1.05 x 31618=33200A.
If you are working out maximum fault level, you might want to neglect the network contribution in case it is upgraded later and depending on the transformer type, it might be included differently (delta-wye doesn't include zero-sequence of the network contribution). Strictly speaking, impedances should be split into X and R because the network X/R will be different to the transformer X/R (Network X/R may be 10, transformer X/R may be 4), but that is probably going to have a very small impact in this instance.

RE: FAULT LEVEL

I prefer the MVA method. Calculate the short circuit MVA of each branch and combine them as admittances.

Utility MVA = 250 = MVAutil

Transformer MVA = MVA rating/Zpu =1.5MVA/.06 = 25 MVA
= Maximum short circuit to the transformer terminals if the primary is connected to an infinte bus.

Combine the MVA's. As admittances, series connected MVA's combine like resistances in parallel. Parallel MVA's add.

1/MVAsc = (1/MVAutil) + (1/MVAtx) = 1/250 +1/25 = 0.044.

MVAsc = 1/0.044 = 22.73 MVA.

At 415V, Isc = 22.73 MVAx 10^6/(415V x 1.732) =31,623 Amps 3 phase, nominal voltage.

For the 105% voltage factor, mulitply by 1.05 = 33,204.

For the fault level with an infinite bus I = 25MVAx10^6/(415V x 1.732)= 34,781A

As stated in the previous post, different X/R ratios can affect the acuracy of this method.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources