Hi All,

I am designing a large slab on ground to the ACI standards, however I have only experience in designing to the EN codes and TR34. When using the ACI approach (unreinforced slab) I am getting a very thick section in comparison to TR34. The reason is that the ACI only allows to design unreinforced slab and TR34 reinforced (bottom mesh). For example using the PCA charts for two racking legs (back to back, 300mm apart) with a load 25000psi (total load for two legs), over 24inch2 total contact area and 96x44inch racking spacing I am getting 10.7inch slab! This is considering FOS 1.7. Not to mention when design the load on the edge of the slab!

For the TR34 approach I am getting 175mm slab with A193 mesh bottom which is ok. But unforunetly I need to comply with the ACI

Any toughs please? Maybe I am getting this all wrong?

Regards
Karol

RE: Slab on ground to ACI codes

(OP)
All,

Anybody can help me in relation to the above please???

Karol

RE: Slab on ground to ACI codes

What is your reference for thinking that an ACI 318 slab does not allow reinforcement? I read 7.12.2.1 as requiring 0.0018*Ag minimum reinforcement for temperature and shrinkage effects. If the members are in bending, there is a minimum reinforcement for that as well.

RE: Slab on ground to ACI codes

fegenbush,
ACI318 does not apply to slabs on ground. There is another ACI reference which does, and I think the OP will get some comment on that, probably after the weekend.

RE: Slab on ground to ACI codes

(OP)
fegenbush ,
I am using ACI 360R-10 "Guide to Design of Slabs-on-Ground".

RE: Slab on ground to ACI codes

"The reason is that the ACI only allows to design unreinforced slab..."

ACI 360-06 pg 30 indicates that when flexural tensile stress exceeds the allowable, you can increase the thickness or provide reinforcement to provide all of the tension indicated by the analysis.

RE: Slab on ground to ACI codes

(OP)
I wonder if anybody can double check if my understanding of the ACI360 standards is correct :

I got a 10.6 inch slab (270mm) based on the following assumptions : safety factor 1.7, concrete strength fc =4500psi (40N concrete), subgrade k=200 pci (10% CBR), Concentrated load P = 25000 lbs (approx 120kN – double racking leg concentration), contact area 23.20in2 (30000mm2 – two baseplate assuming 150x100mm each).

The 270mm slab on ground sounds very thick to me for the loading provided. Thus not sure if I am using the ACI standards correctly?

Regards

RE: Slab on ground to ACI codes

(OP)
Lads,
Really need help on this!

RE: Slab on ground to ACI codes

Check out 'Designing Floor Slabs on Grade'. Lots of great information and walkthroughs for designing slab on grade for wheel loads, post loads, etc.

link at amazon.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources