Smoke Control Panel without UL or any other NRTL listing?

Smoke Control Panel without UL or any other NRTL listing?

Smoke Control Panel without UL or any other NRTL listing?

(OP)
A UL 508a panel shop has been assigned to build a smoke control panel. They can't stick a 508a UL label on it, that is prohibited. UL 864, category code UUKL is what applies to smoke control panels. No panel shop can do UL 864 stuff, that is a standard that must be certified by submitting samples to UL and having extensive testing done.

Questions:

1) If the contractor for whom the panel is to be built gives a written waiver of responsibility for the non-label issue, would you build an unlabeled smoke panel?

2) If the local AHJ gives a written OK for the unlabeled smoke panel, would you build it?

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Smoke Control Panel without UL or any other NRTL listing?

Nothing in Section 909.16 in the 2009 International Building Code requires that the smoke control panel be listed.

RE: Smoke Control Panel without UL or any other NRTL listing?

(OP)
Thanks stookey,

I couldn't find anything in there either, but NFPA 92 is being enforced:

6.4 Smoke Control Systems

6.4.1 Control systems shall be listed in accordance with ANSI/UL 864, Standard for Control Units and Accessories for Fire Alarm Systems, category UUKL, for their intended purpose.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Smoke Control Panel without UL or any other NRTL listing?

Dave:

I can't offer much more because my jurisdiction doesn't adopt NFPA 92. We have over 100 high-rise buildings and most have some active smoke control systems.

Given the fact that even with a prescriptive design that smoke control systems are engineered, the jurisdiction should understand the panel is nothing more than a control component for a system that will activate and respond before the FD is dispatched.

Is this a high-rise or a large Group A occupancy?

RE: Smoke Control Panel without UL or any other NRTL listing?

(OP)
Thanks again Stookey. I'm mostly in agreement with you.

The building is this thing: http://www.victorianweb.org/art/architecture/iron/...

Sort of an ancient covered shopping mall that's being turned into apartments called "micro-lofts." It's three stories high.

I'm going to go ahead and ask the fire marshal. But our company's attorneys will have the final say-so...

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Smoke Control Panel without UL or any other NRTL listing?

Interesting. If was the Fire Protection Engineer on the project, I would present the analysis of applying the requirements in International Existing Building Code to avoid the atrium smoke control system. I think I could persuade the code official to allow a more robust sprinkler design to avoid attempting to retrofit smoke control in that building.

RE: Smoke Control Panel without UL or any other NRTL listing?

(OP)
Wish you were here, stookey.

Thanks tons for your input!

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources