I'm using ASCE 7-10 to calculate the seismic loads acting on a structure. The structure is a moment frame (OMF) that supports an elevated bin that stores fly ash. Based on this useage, I classified this structure as a "nonbuilding similar to a building" (Chapter 15 provisions). I came across an interpretation issue.

NOTE - this is Seismic Design Category B and special seismic detaiing requirements are not desired (per AISC 360 only....not AISC 341).

According to ASCE 15.4.1, note 1a, the structural system can be selected from either Table 12.2-1 or 15.4-1. Table 12.2-1 has a category (H) that is for buildings NOT specifically detailed for seismic resistance & R = 3. Table 15.4-1 does not have such a note......instead, Table 15.4-1 allows detailing per AISC 360 under the "unlimited" height category, which requires R = 1 for a OMF.

My interpretation is that the R = 3 (Table 12.2-1 Category H) is a general recommendation for anything that hasn't been specifically detailed for seismic resistance. However, some structures require a R value of less than 3 even if special detailing requirements aren't followed. In essence, Table 15.4-1 overrides Table 12.2-1 in this case. (This is also demonstrated in various structural systems that have R < 3 in Table 12.2-1.)

Am I interpreting this correctly?

RE: ASCE 7 - Seismic Design (R < 3) of Nonbuilding Similar to Building

I don't believe your interpretation is correct. The R-values are identical between Table 15.4-1 and Table 12.2-1 for the basic systems. The R-values are different only for the "With permitted height increase" and "With unlimited height" cases. In your case, because you are Seismic Design Category B, you have the option of using R=3 from Table 12.2-1 or R=1 from Table 15.4-1 and avoid the seismic detailing requirements of AISC 341 in either case. Using R=3 is the obvious answer. Had you been in Seismic Design Category D or above, wanted to use an ordinary moment frame, and wished to avoid the seismic detailing requirements of AISC 341, Table 15.4-1 permits that option but 'punishes' you by requiring the use of R=1.

RE: ASCE 7 - Seismic Design (R < 3) of Nonbuilding Similar to Building

(OP)
I see it now. I typically deal with low seismic categories (A or B) so my options are usually limitless. In a case where I would have SDC D, I couldn't use a OMF for a building system.....I would have to use a special type of moment frame. However, in this same case, I could use a OMF for a nonbuilding, but if I wanted to still stay with AISC 360 detailing requirements, I'm "punished" by using a lower R value.

Sometimes it just takes another set of eyes......thanks!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources