Summing module reading different weighted 4-20mA signals. Hardwired solution to get correct sum?
Current monitors sense large dc currents from separate paths. They sum into a summing module whose output value reports on a meter and a PLC. We have a new DC current path will have more than twice the current as any of the old paths.
We want to pull this info into the existing summing module that can't be programmed for individual inputs. I thought about pulling this info into 2 separate inputs on the summing module... Is there a hardwired solution here?
See the attached sketch.
RE: Summing module reading different weighted 4-20mA signals. Hardwired solution to get correct sum?
All your current sources are floating and that means that you can just wire them together and they will sum up nicely.
It is the Thevenin equivalent of adding DC voltages in series.
So, all you need to do is wire all current sources together and read the resulting current.
Of course, you need to scale all signals so that 1 mA means the same thing. That condition is not satisfied in your sketch, where the lower current source is scaled differently from the other ones.
You also need to make sure that the sum of your currents doesn't exceed the range of the summing node (which is probably 20 mA).
There are loop insulators if you want to keep the current sources isolated.
Gunnar Englund
www.gke.org
Clarification: In parallel, right?
Gunnar Englund
www.gke.org
TTFN
Gunnar Englund
www.gke.org
Change the two low ones from 15,000A:20 mA each to 35,000A:20 mA each. All the same ratio, no need for a summing / scaling device.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
Gunnar Englund
www.gke.org
Best to you,
Goober Dave
