PLC restarting
PLC restarting
hello every one:
I have PLC seimens S7-300 that installed with machine
but the PLC gives wrong commands in certain module , it is possible to restart the PLC without losing the user data in micro memory data
what is the major effect of this restarting
RE: PLC restarting
There is not many major effect of this procedure on the CPU itself. It would go through its boot-up routines, and user-define boot-up tasks (if programmed). Depending on the user defined boot-up tasks, the rebooting may be a bit stressful for the machine it controls.
Please note that, your problem is a bit fishy. Are you sure it is a problem from the program? Any cards bad? Any field device mal-functioning? Do you have the PLC source code? What you are suggesting is not acceptable as an operation procedure.
RE: PLC restarting
the tow motor is same function
the first motor receive the command from PLC to run at certain period and then deactivate
but the second motor continually receive the command without stop ,I've checked the all connection and switches all is correct
I replaced the PLC card but nothing new,
if the problem from PLC program ,what can I do??
RE: PLC restarting
What this means is that you have a switch or wire or something external that is causing the problem. You say, "I've checked all the connect and switches all is correct", but it's not clear to me that you've checked their actual function and continuity right up to the PLC terminal screws. Have you used a meter and traced the actual signals?
If you're ABSOLUTELY sure the wiring is flawless and you've swapped in a new PLC, you'll need someone who understands the PLC and the development tool to work with it.
Keith Cress
RE: PLC restarting