Grounding & Protection Scheme for Parallel Generators

Grounding & Protection Scheme for Parallel Generators

Grounding & Protection Scheme for Parallel Generators

(OP)
Dear Folks,
We have three 3-MW, 4160 V, 3 phase geneators.  I would like to know the proper grounding and protection scheme for parallelling those generators.  We are experiencing high circulating current (appr. 300A) when two generators are running in parallel and the load is very small (appr. 50A).  Does it sound like a grounding problem or something else?
Andy

RE: Grounding & Protection Scheme for Parallel Generators

The problem you are describing sounds like reactive power circulating because the two voltage regulators are fighting each other trying to maintain voltage setpoint.  When the generators are operated in parallel, the voltage regulators need to be designed and configured to share the reactive power load.  This is typically done in a reactive power droop mode using paralleling CTs on each generator.  Check the Basler website www.basler.com for more information on parallel operation.  

As far as grounding goes, some type of resistance grounding should be used.  The exact configuration depends on your system.  The brute force approach is to put a grounding resistor on each generator.  This increases the ground fault current when multiple generators are operating and increases potential problems with harmonic currents.  An alternate approach is to install switching such that only one resistor is in use at one time.  

If you have a grounded transformer on the bus that will always be energized, you can put the grounding resistor there, and leave the generators ungrounded.  

Hope that helps a little.

RE: Grounding & Protection Scheme for Parallel Generators

Suggestion: I just would like to add a bit to the previous posting. One generator is preferred to have system grounding. It could be high-resistance or medium resistance system grounding. The other generator neutrals are not connected to the neutral bus but they may have a circuit breaker plug in arrangement on stand-by just in case needed when the one generator with the system grounding is being out of service.

RE: Grounding & Protection Scheme for Parallel Generators


Possibly IEEE C62.92.2-1989 Grounding of Synchronous Generator Systems  ISBN 0-7381-0933-9  
  
And, IEEE C37.101-1993 – Guide for Generator Ground Protection  ISBN 0-7381-0901-0  
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources