Special Corner Reinforcement
Hi all,
I need help understanding something in ACI 318-08 R11.1.3.1. I have a suspended slab hanging on all four sides from structural walls. It looks exactly like Figure R11.1.3.1(e). The last paragraph of R11.1.3.1 indicates that for this hanging condition, "Shear within the connection should also be investigated and special corner reinforcement should be provided."
So my question is, what does "special corner reinforcement" mean here? Does it mean to make sure the wall's vertical bars extend into the slab and are properly anchored (hooked) to the slab's horizontal reinforcing? Does it mean to provide vertical or horizontal shear reinforcement in the connection's space?
To greatly simplify construction, I am detailing the slab to be poured first, and the supporting walls to be poured on top of the slab. My slab also requires shear reinforcing (it's a heavily loaded industrial slab, and we can't go any thicker). I am planning on extending the slab's shear reinforcing through the portion of the slab below the wall connection (I know I have congestion issues to worry about here).
I appreciate any input on this. If possible, please also provide an explanation and any supporting references to your interpretation on this.
Thanks much!
Thanks much!
RE: Special Corner Reinforcement
BA