Repair of Corroded Tube Column Bottom and Base Plate
This is an existing building with a column in need of repair. The remaining rust can be scraped and corrosion inhibitor applied. A nearby drain outlet is the cause and will be dealt with.
The column is HSS 6 x 6 and supports about 53k (D+.25L) at the moment. W 16 x 26 beams frame into each side and one side has a diagonal HSS 5 x 5 framing in (see pictures).
I'm looking for input on two repair options and shoring guidelines:
Option 1: shore column, remove rusted bottom of the column, install base plate/anchors, weld plates to side of HSS column and base plate on each side.
Option 2: remove plate on one side of column, install L shaped plate (welded 1/2" plates or something... to be calculated) welded to column and anchored to footing, cut plate on 2nd side, install L shaped plate... etc. until all 4 sides are supported. The goal of this option is to eliminate shoring requirements.
Shoring: My client is the contractor on the job and I proposed Option 1 which, after inspecting the area for himself, said was the same thing he was thinking. He said he could do it. Myself, I'm worried about the shoring, especially with the diagonal tube preventing jacks from getting a good bearin surface.
I'm not familiar with shoring methods. Is this a clean and clear cut shoring job? Would I just check the beam shear connections for strength as well as beam shear and web crippling/buckling? How does the diagonal effect things? Is Option 2 valid?
I appreciate any guidance on the matter. I didn't see any old thread on the topic but direction towards one would be appreciated as well.
Kirk G Hall, PE
RE: Repair of Corroded Tube Column Bottom and Base Plate
Kirk G Hall, PE
BA
You may not have to jack if you can bust out the concrete below the base plate. Then all you need to do is install some cribbing and shim it tight against the W16.
Kirk G Hall, PE
BA
It also look like the tube has a source of water inside, so sort that out to prevent a repeat.