Alternating Real vs PLC

Alternating Real vs PLC

Alternating Real vs PLC

(OP)
I'm in the process of coming up with a 3 motor alternating scheme with a trip indicator.  I am wondering if it is possible to do it with relays or if it would be easier to use a PLC.

RE: Alternating Real vs PLC

You can do this with relays but a PLC would be easier. Also with PLC any changes are faster by reprogramming than rewiring.  PLC add more advantages in the short and long run. By the time you buy all your relays switches and lights. You could have bought a micro PLC. Add some more money get a small display, now you have an enunciator with time stamp. Also a runtime counter, changeable seq. & ect..

Although relays wont go into fault after a thunderstorm.  

RE: Alternating Real vs PLC

Agreed.

I assume that coordinating these relays will become tedious depending on how many are used. Futhermore, the hardwiring bit becomes a headache when minor changes have to be made very frequently..

Condideration: optoisolators for PLC protection

RE: Alternating Real vs PLC

I've seen a combination of both, the PLC will:
1. drive control relays (due to the contact rating of the plc's built in relays) and,
2. perform all the logic, annunciation functions

Make sure the logic is failsafe (e.g. if it is driving lube oil pumps: the pumps run when the system is tripped (control relay is DOTR - dropout to run), the only way to stop the pumps will be to open the MCC breaker, if it is driving fuel-oil pumps the control relay MUST be PUTR (pick-up to run) otherwise you'll be pumping fuel into you-do-not know-what...

The thunderstorm problems I had were always troubleshot to poorly installed shielding and grounding system.

HTH
Saludos.
a.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources