Hi,
I have been told that if the distance between the inverter and the motor is greater than 100m it's needs a choke and if its greater than 300m it needs a filter. Can someone explain these please?
Thanks
I have been told that if the distance between the inverter and the motor is greater than 100m it's needs a choke and if its greater than 300m it needs a filter. Can someone explain these please?
Thanks





RE: Inverter (vfd)
There are two types of information: Confusion and True Information. Sort out the 95% confused and you will be close to understanding.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Inverter (vfd)
Also, do you have any EMI restrictions. This will also limit cable length depending on category you need to meet.
RE: Inverter (vfd)
You can analyze this to death with every drive / motor combination, or you can adopt useful rules of thumb. My personal rule of thumb is to always use a load reactor regardless of cable length (and an inverter duty motor). They are inexpensive and provide multiple benefits.
RE: Inverter (vfd)
For the dV/dt effects it seems that the longer the cable, after approx 42 metres, the better. But then the voltage drops in the cable will certainly become a factor at 300m.