Hi peepz, just a quick one. What is the difference in performance between a 250 kw, 525V motor and a 250 kw, 6600V motor?

Thanks.

RE: Motor Supply Voltage and Performance

Not much. No point in using a 6 kV motor if you have a 525 V grid. If you don't - then an MV motor may make sense. But usually, they need to be quite a bit larger to motivate the more expensive cables and switchgear.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Motor Supply Voltage and Performance

One issue on the side of MV, if you have 6600V available already, but you have to buy a transformer to get 525V (or 575V?), then there will be losses in the transformer to consider for overall throughput efficiency compared to running at 6600V. The cost of those losses, compared to the added capital equipment cost of the 6600V equipment as Skogsgura pointed out, would need to be evaluated.

But from a motor standpoint, kW is kW is kW, no difference in performance.


"Will work for salami"

RE: Motor Supply Voltage and Performance

Also consider cost of labor since qualifications for working at 6.6 kV vs 0.525 kV is different in some jurisdictions.

RE: Motor Supply Voltage and Performance

If you would intend to start the motor D.O.L. [direct-on-line] you could encounter a large starting current, which in turn could produce a very large voltage drop and disturb the other motor already functioning. However, usually 250 hp is still possible.
By the way, since copper is the more valuable than insulation, the medium voltage cable could be cheaper.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources