For low preessue steam and condensate pipe risers in a 250 ft tall building what type of expansion compensator is best to absorb 4 inches of pipe expansion?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Steam piping expansion compensator
|
Steam piping expansion compensatorSteam piping expansion compensator(OP)
For low preessue steam and condensate pipe risers in a 250 ft tall building what type of expansion compensator is best to absorb 4 inches of pipe expansion?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: Steam piping expansion compensator
I brought this back to the head of the list for discussion because it sounds similar to
Thread378-34510
Regards, John
RE: Steam piping expansion compensator
RE: Steam piping expansion compensator
There's no question that an improperly designed joint, or putting a joint into a situation that it cannot handle, is certainly going to lead to problems.
However, there are thousands of expansion joints working well in service all over the world. I would bet in most of those cases, the expansion joint is not only the best solution, but quite possibly the only practical solution.
Now, if a joint is not needed (i.e., and expansion loop can effectively be added to the design to handle the movements) then those options should be taken first.
But, it's clear there are large pockets of closed minds all around when it comes to expansion joints becuase one joint failed one time for someone, for reasons that were probably not fully investigated.
Perhaps groups like EJMA need to be more proactive in educating design companies and end users on the proper design and use of these joints.
Of course, joint companies are sometimes there own worst enemies. I remember one sales guy making a presentation trying to convince a room full of stress engineers that we should be using expansion joints instead of expansion loops for pipe racks. I don't think we've bought much from that company.
Edward L. Klein
Pipe Stress Engineer
Houston, Texas
All opinions expressed here are my own and not my company's.
RE: Steam piping expansion compensator
RE: Steam piping expansion compensator
I kinda thought the discussion would go this way.
For the original question regarding risers in a building (where they often go up through the stair wells) I thought the approach I outlined in Thread378-34510 was OK. I really don't like to see EJ's in this (commercial or institutional buildings) application because they usually do not get proper surveillance and care (and they are in "harm's way"). I would much rather see welded pipe expansion "loops" (sometimes just a little offset will do) and it seems that y'all feel the same way.
It seems to be a good idea to remind readers of this thread that EJ's are one third of a "system". When you decide to install and EJ you need to remember that it is necessary to think about where to locate guides and where to locate "anchors" (the entire topic of what constitutes an anchor should be saved for another discussion). The EJMA Standards do a good job of explaining this concept but not enough "designers" (another topic for discussion) read and understand the EJMA Standards.
Expansion Joints fail either because the three-part "system" is ill designed in the engineering stage (or it is an incorrect application for the EJ specified) or they are improperly installed, or both. Often the "designer" calls the manufacturer's rep and asks him/her what to specify - bad idea. Or the "designer" picks the wrong EJ for the application. EJ's have a finite life like any piping component - if they are improperly applied or improperly installed, that fatigue life will be used-up in a sudden hurry (too often, less that one load application). If the "designer" does a creditable job of specifying the EJ system and the drafter (remember those? - NOW it is an insult to call a "designer" a drafter) gets it into the drawing correctly, someone still needs to get out and inspect the final installation - this is not done enough. Once the EJ is in service, it needs to be put on the maintenance list for routine checks of the joint, the guides and the "anchors". Sometimes the EJ is damaged later by adjacent construction projects - the bellows element is fragile, to form it the metal was formed and forced into the plastic regime of the material (by some definitions plastic deformation constitutes a "failure" in a piping component). If the bellows is not supplied with a protective cover it is open to damage (weld splatter, stuff between the convolutions, etc.). So we end up with many EJ "failures" (or are they "designer" failures?) and EJ's get a general bad (often undeserved) reputation.
I was hoping that Dr. Chuck Becht would wander into this discussion as he was the principal writer of B31.3 Appendix X, and this was the topic of his PhD dissertation.
Getting back to the original question, I still think designing the riser to include welded pipe offsets to accommodate the expansion/contraction is the most cost effective solution.
Best regards, John.