OVERHEAD WATER TANK AND CISTERN TANK COMBINATION
GOOD DAY!!
I just want to raise a question here bout overhead tank combined with a basement cistern.
I was assigned to design a 15,000 gal capacity sprinkler system, the problem was the source of supply consists of this: two(2) 5,000 gal overhead tank and one(1) 5,000 gal capacity basement cistern tank. The building is three-storey approximately 40 ft high. How can I meet the system requirement for the design, specifically to combine the upstream and down stream supply..
Appreciate to get feedbacks...thnks.
RE: OVERHEAD WATER TANK AND CISTERN TANK COMBINATION
2) Disregard the basement cistern tank and use a municipal water supply to fill the overhead cistern tanks? Employ option 1 to meet the sprinkler demand
3) Calculate the hydraulic demand at the 3rd floor and if the static and residual pressures are great enough from the municipal water supply to meet the hydraulic demand, disregard the cisterns completely?
Have you calculated the hydraulic demand for the residential sprinkler system using NFPA 13R? Based on a 4-sprinkler design area your total flow should not exceed 100-120 GPM assuming 20 ft x 20 ft sprinkler spacing.
the system demand is 198 gpm w/o considering the hose allotment and demand pressure of 42 psi. if the overhead tank alone, only 20 psi approximately is available against a demand of 42 psi, from my point of view the overhead tanks are not sufficient enough to meet the system demand.
here is installation scheme, a 10hp fire pump at the ground floor to supply 5,000 gal from cistern @50 psi. the total capacity is 15,000 gal for 30 mins. minimum running time. 5,000 gal from the cistern will only last more or less 10 mins. 10,000 gal for two overhead tanks is sufficient enough to supply the remaining demand. but, it cannot meet the pressure demand of the system. do i need to add a booster pump for the overhead tanks?
sir, can i ask for a link for that FM data sheet for break tanks?
thanks in regards.