Blocking Roof Sheathing Edges: Roof Sheathing fastening Schedules

Blocking Roof Sheathing Edges: Roof Sheathing fastening Schedules

Blocking Roof Sheathing Edges: Roof Sheathing fastening Schedules

(OP)
T325 Roof Sheathing Fastening Schedules for Wind Uplift (Published by APA) Table 1
has the following footnote:
"When wind speed is 100 mph or greater, block panel edges perpendicular to gable-end-wall framing members in the first two bays of framing. Blocking shall be spaced a maximum of 4 feet o.c. (Wood Frame Construction Manual, Section 3.5.5)"

Question 1: Is the intent to secure the panel edges with respect to increased uplift or is it to increase the shear capacity in an otherwise unblocked diaphragm?

State code (amendment) allows for elimination of this blocking when using 5/8" T&G sheathing.

Therefore one would assume that it would be for uplift since the T&G would not transfer shear; would reduce potential for buckling at shear failure though.

I have also seen a variation of the of the amendment that calls for maintaining the blocking at the ridge and soffit(Zone 3 highest pressure), but eliminating it in between.

I have a detail that will transfer roof shear to the bearing wall while maintaining ventilation.

My problem would be at the ridge since 2x blocking on the flat would block the 1" air space; vaulted ceiling 2X12, 10-1/4" insulation, drywall attached to 2X12 rafters creating a confined space.





RE: Blocking Roof Sheathing Edges: Roof Sheathing fastening Schedules

This is for uplift. The 4-foot perimeter is an approximation of the end/edge condition loading in ASCE 7 and the basic building codes based on IBC model code.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources