(OP)
I was recently reviewing a ground grid study for an indoor installation and saw something that struck me as odd. The ground grid is installed beneath the basement, air cured, concrete floor of a building. There is steel re-bar inside the concrete slab. Yet the study still lists the resistance of the slab as 10,000 ohm-meters. This seems high to me.

Has anyone had previous experience with this type of installation that could verify whether this is or isn't a plausible resistance value for air cured concrete with re-bar?

References to technical documents would be much appreciated. I have already looked through the office copies of IEEE 80, IEEE 81, IEEE 665 and the IEEE Green Book. I so far haven't been able to locate anything indicating the resistance of air cured concrete for indoor installations.

RE: Ground Grid - Indoor installation

Concrete mixes using Type III Portland cement with ternary combinations of Class F fly ash, silica fume and slag could present up to 1000 ohm-m resistivity. See:
http://www.claisse.info/2010%20papers/m19.pdf
Usually under the concrete floor, it is an isolation layer –polyethylene or rubber
of 2-5 mm thick and this layer of high resistivity could influence the resistance measurement.

RE: Ground Grid - Indoor installation

TSun,
Just for my own curiosity, why there is a copper ground grid under the steel re-bar concrete basement at the first place?
What type of electrical installation do you have?

RE: Ground Grid - Indoor installation

(OP)
It is a commercial building with indoor 15kV equipment. With the way they modeled the room, the ground grid is necessary to keep step and touch potentials to an acceptable level but I am not sure that the room was modeled correctly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.