Cracked Wood Rafter

Cracked Wood Rafter

(OP)
Thank you for consideration.

I viewed a cracked rafter in an attic. Crack is at bottom of 2x8 rafter which spans about 19 feet and spaced about 16 inches on center. The crack does not appear to be fresh. I have been told the crack is due to wind. I am not buying it. The wind speed was about 60 mph and there were about 5 shingle tabs blown from roof. Metal ridge vent did not blow off of roof. I suspect it would prior to wood framing cracking from wind load.

So, why the cracked rafter? Could it be; inadequate lateral bracing?,,,undersized for span? knots/imperfections in wood?..... bundles of shingles laid upon it during construction (but 8:12 roof slope)?....The crack is located on rafter where it meets wall below and where it meets ridge. I have attached photographs, please view them and comment.

thanks.

RE: Cracked Wood Rafter

To me that lower crack looks really old. the grain is also really bad looking on it. the top crack looks to be the result of 'shake' in the board (a grain delamination from wind bending in the tree state or improper drying). The seat cut is not right, there is very little support for any kind of load on that rafter. It needs more bearing surface to rest on. Looking at the pictures; I don't think wind had anything to do with this crack, it's been there for years. It's a combination of back wood and bad carpentry.

RE: Cracked Wood Rafter

Well, a 19 foot span for a 2X6 could be a bit much (more likely than not, is), depending on the snow load and roof slope.

As for the crack, it has a notch in the end that bears on a 2X plate, and the failure occurred at the notch which is a stress riser. Looks like quite a substantial notch for the depth of rafter too.

As for knots, there is not enough detail in your picture to see any, at least on my computer. Maybe someone else will have better luck.

As for the wind load, I doubt it. More likely a vertical load.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Cracked Wood Rafter

msquared, I think they're 2x8's. Still a long span, though. jimjxs, do you get much snow your way?

RE: Cracked Wood Rafter

Could have just been installed that way. Some carpenters do that sort of thing rather buying (or cutting) a new one. Doesn't look like any reasonable damage source as the damage is severe and the neighbors are fine. Is the rafter displaced in any way? Is this an insurance claim?

______________
MAP

RE: Cracked Wood Rafter

Archie264:

You're correct, but my comment about the span still stands - just not quite so critical. I would have been much better with 2X10's, or 2X12's cconsidering the end notching.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Cracked Wood Rafter

msquared,

Oh, I definitely agree. I was about to post something similar to what you wrote except only focusing on the span. One issue at a time is all I can manage; your response was more complete.

RE: Cracked Wood Rafter

(OP)
THANK YOU ALL FOR THE RESPONSES.

DOES ANYONE KNOW OF THE CODE SECTION (IRC) WHERE RAFTER BEARING IS ADDRESSED? I WOULD LIKE TO REFERENCE THE APPROPRIATE CODE SECTION WHEN CONTRIBUTING THE CRACK AT BOTTOM OF RAFTER TO INADEQUATE CONSTRUCTION.

THANKS, ALL.

RE: Cracked Wood Rafter

Actually, this gets into good connection design practice more than end bearing values, which would be covered by the current NDS. In my AITC Timber Construction Manual, the third edition, on pages 7-702 (Detail A5), and page 7-703 (Detail A7), this condition is specified as a definite NONO. Similar details can be found in the 4th Edition on pages 8-780 and 781.

By the way, no worries, but when you post, don't use all caps. That's considered screaming, and a lot of us here have hearing aids! :)

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Cracked Wood Rafter

Commenting further, the better, structurally acceptable connection would have been to flat cut the rafters, bear them directly on top of the plate, and use angle clips or similar Simpson connectors to nail the rafter off to the plate.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Cracked Wood Rafter

Strange detail. Hard to tell with the insulation there, but is the rafter double cut to bear on both plates (the wall plate which the ceiling joists bear on and the one on top of the ceiling joists which we can see in the photos)?

RE: Cracked Wood Rafter

Look in NDS for notching of the bottom of beams/joists/rafters, particularly at the bearings or in high tension regions. At the lower bearing plate, that rafter is effectively notched about 60 or 70% of its height, at least that is the effect of how it bears on the plate. The horiz. shear stress is very high at the bearings and all the more so when you have an actual notch or that notch affect. Your detail is literally tension perpendicular to (across) the grain, also not allowed. Is the crack up at the ridge in the same member? That is at least supported by a ridge board and would/should be less likely to crack. That may just be one bad joist member. But, if they piled large stacks of shingles right over that joist, that might have caused high shears on that one member also. I agree with MikeM on several accounts: the bottom bearing on those rafters should have been slope cut without a notch, and they should have been bearing on the plate under their lower edge, not at their upper edge. Then light angles applied btwn. the rafter and the bearing plate to pick up the thrust. You might want to rip one edge of a 2x6 or 2x8 to 8/12 to match the rafter slope. Lay this member flat on the clg. joists and push it in under the rafters and nail it off to the clg. joists, for some added bearing area on the underside of the rafters. This member doesn’t have to be a 2x8 as long as you can nail to the clg. joists under (along side) the rafters.

RE: Cracked Wood Rafter

The 2003 IRC (the most current one I have) Section R802.7.1 "Sawn lumber. Notches in solid lumber joists, rafters and beams shall not exceed one-sixth of the depth of the member, shall not be longer than one-third of the depth of the member and shall not be located in the middle one-third of the span. Notches at the ends of the member shall not exceed one-fourth the depth of the member...."
So the rafter, per this section, must start bearing at 1/4 the depth from the inside of the member.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.

RE: Cracked Wood Rafter

It looks like the bottom may have water damage/rot (white residue, dark colored wood). It also looks like the lumber was milled a little off, notice the ridge that runs the length. I have floor joist that have delaminated at these locations.

RE: Cracked Wood Rafter

(OP)
woodman88,
Can you provide me with a copy of the details?
thanks,
jimjxs263

RE: Cracked Wood Rafter

(OP)
msquared48,
thanks for the attachements! They were both the same and started with detail A6. Can you also send detail A5 on p. 7-702? thanks again!

RE: Cracked Wood Rafter

Are we sure there isn't something else going on? All of the ends of the rafters appear to have short cracks running parallel to the grain. I have never seen cracking in wood like this. Also as mentioned by lardman363, there is discoloration and white residue.

RE: Cracked Wood Rafter

There could be other factors, but the detail is very bad. Whether the cracks are fresh or old, there seems to be a clear need for remedial action throughout.

BA

RE: Cracked Wood Rafter

OK, this thread is getting so much traction I had to revisit the original question.
Wind? Not likely. I would expect more damage to the other rafters too this this much on one. Additionally, the overframing at this area would have something to say about this if if were true. The crack is not very "fresh" looking either. So if you are looking for a recent "NATURAL EVENT" or "ACT OF GOD" this is not it. That is unless something strategically fell on it due to the wind. But not damage the others?

My Official Guess: a bad detail with a improperly placed impact construction load and possibly a bad board to boot. I'm calling it "the convergence theory". The top crack is the most interesting to the bad board part. Almost looks like 1st: damaged, 2nd: water got into it and 3rd: then was left in the sun to bake before installing. The way it is separated along the grain and has a bit of a warp to it... The bottom most likely was damaged in place. Strange location within the roof for this one rafter to be singled out. Maybe someone dropped a sheet of plywood or packages of shingles or stepped on it wrong. Wouldn't take much -the bad detail clearly contributed to its demise.

jmjxs263: what did you report?

______________
MAP

RE: Cracked Wood Rafter

I think we all realize the detail is poor. NDS limits end notches to 1/4 the depth and I have heard of 1/3 depth used frequently on residential projects. These rafters have been notched closer to 3/4 their depths. Another reason this detail is poor is it induces tension perpendicular to the grain when resisting thrust(if the notch resists the force). My point was that one needs to be certain what the caused of failure was prior to suggesting a repair.

Maybe those smaller cracks are from tension perpendicular to the grain caused by the end condition? Then a better detail would solve the problem. I question why a notch is required. Resist the thrust a different way.

RE: Cracked Wood Rafter

Rafter framing is funny. If you sit down and do the engineering, most of the connections just don't work. A lot of times, the thrust reactions are enormous. If you get into multiple gables and levels, the engineering is almost impossible.

The IRC has huge holes in it as far as rafter framing goes. The prescriptive code does not properly address the collar tie connections. I started a job using prescriptive IRC design and scrapped it when I saw a 10x factor of safety concern.

I won't even touch a rafter framed project unless it is very simple. No one knows how to build it and an architect doesn't understand how to design it. Trusses are the way to go.

In your particular condition, the joist cracked because the bearing condition is causing stress across the grain.

RE: Cracked Wood Rafter

Well, on that note, residential structural engineering in general can be a real head-scratcher. Many situations exist that don't work "on paper" and yet they've held up for decades. Sometimes I wonder if wallpaper has a structural component that holds the whole thing together. Residential structural engineering can really be it's own sub-specialty.

RE: Cracked Wood Rafter

I agree. Some stuff "just works". Doing a full analysis doesn't take into account all of the factors in a design. That is often impossible.

What concerns me is the slippery slope of prescriptive design.

"This (accidentally) worked before, let's do that 100 times"
"If that works for a 10' beam, I bet it would work for an 11' beam"
and so on

The ICC has caught some of these errors and has tried to fix them at the reluctance of builders. For example, basement wall bracing was addressed in IRC09 to change wall bracing from 1/2" bolts at 6' o.c. (not even close to working). I was happy they changed it since it was one of my gripes. After enough prodding by builders, they removed the structurally adequate section from the code. "It just works". Sure it works, but try that on a 15' wall and tell me how that works out for you.

/rant

Be careful. Sometimes the prescriptive stuff doesn't work.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources