CT typical resistance value
Hi all,
Can anybody suggest typical values for the secondary resistance of these CTs?
50/1 A 15VA Cl. 1
50/1 A 10VA 5P20
These are fairly old CTs and I can't find the documentation from the manufacturer. Nor can I measure it because the plant cannot be stopped right now. My guess is something like 0,2 ohm, and in any case less than 1 ohm.
RE: CT typical resistance value
If you know the number of turns and approximate dimensions of the cut and secondary tails you can calculate the figure using the standard resistivity value of copper.
Typical values for the resistance per turn of a CT are in the order of 0.0025 Ohms/turn. It is very unlikely that you are at 1 Ohm for your CT secondary resistance, and probably also below 0.2 Ohms.
Afroeeng:
Thanks, unfortunately I don't have the data to make those calculations.
Mgtrp:
That is more or less what I was thinking. I'll assume 0,2 ohm and probably I'm still on the safe side. Many thanks.
Not to split hairs, but not all CTs are window-type CTs. For a HV or MV CT, you may not have any way of knowing the number of secondary turns.