Jobs

Vertical Itt 500 galon fire pump

Vertical Itt 500 galon fire pump

Vertical Itt 500 galon fire pump

(OP)
Hello Everyone.
I am installing a 500GPM Vertical in-line pump from A-C Fire Pumps. On the suction side I have 6" main, but the pump is 4". It might sound like a stupid question, but, should I put an eccentric reducer or concentric reducer?
Thank you!

Regards

Oleg.

RE: Vertical Itt 500 galon fire pump

From NFPA 20, 2013 ED
4.14.6.4 Eccentric Tapered Reducer or Increaser. Where the suction pipe and pump suction flange are not of the same size, they shall be connected with an eccentric tapered reducer or increaser installed in such a way as to avoid air pockets.

****************************************
Fire Sprinklers Save Firefighters’ Lives Too!
Interested in “Hands On” Fire Protection Seminars with live fires visit www.chubb.com/lcu for information.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources