Electrical Motors - for use in India
|
Electrical Motors - for use in IndiaElectrical Motors - for use in India(OP)
Considering shipping some equipment to India - would the electrical motors be useable there - same power requirements?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
|
RE: Electrical Motors - for use in India
Step 1) Look up the voltage used in India.
Step 2) Match it.
"Will work for salami"
RE: Electrical Motors - for use in India
This customer had huge problems with bearing currents in an application that didn't present any problems at all in other places. It turned out that voltage across the bearings was zero.
Zero is usually a good thing. But not if the reason for zero volts is hot grease. So hot that the oil film was too thin to insulate. Continuous conduction all the time led to EDM and premature bearing failures.
You may need High Temperature Grease and, perhaps, common-mode filters. Check with end user what ambient temperature the motors are supposed to work in.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: Electrical Motors - for use in India
I found the following on an internet search, don't know if could be related to your comments about high temperature operation.
India uses 240 V and 50 Hz
US 240 V and 60 Hz
Using a 60Hz motor in 50Hz duty.
w) It will turn 20% slower.
x) Cooling will drop dramatically.
y) The load's horsepower requirements will drop, possibly dramatically.
z) V/f will increase possibly causing a large increase in current draw.
Make sure the load will still do what is required of it when running slower.
The cooling will reduce dramatically. Is it enough to matter? This depends on how the load has decreased. If the hp requirement dropped because the load has decreased the current will drop and less heat will be released internally. You would want to take temperature measurements until the motor reaches a steady state temperature running in its new frequency application.
The most serious issue is the V/f issue. The V/f will increase. Likely enough to cause a large increase in the motor's current. This coupled with the reduced cooling may cause rapid overheating.
RE: Electrical Motors - for use in India
Step 1) Look up the voltage used in India.
Step 2) Match it.
If you send a single phase (because you mention 240V) motor to India that was designed for use in the US, it is doomed to fail.
Buy a 230V 50hz motor for your machines going to any country outside of North America. Or use 3 phase, that is easier to deal with (long story, but let us know if you want to consider it). But either way, you will need to evaluate what effects your machine will have from the motor running 20% slower. My crystal ball cannot see what your machine is, sorry.
"Will work for salami"
RE: Electrical Motors - for use in India
For a hoist or conveyor, when changing changing the speed from 60hz to 50hz, the device will run at 83% of the original speed. The slower speed may or may not be be a problem depending on the customer requirements.
However, for a centrifugal compressor, pump, or fan, the flow will be reduced proportional to the reduction in speed so that the new flow will be 83% of the original flow. More importantly, the output pressure (or pump head) will be reduced proportion to the square of the reduction in speed so that the new pressure will be 69% of the original pressure. Depending on the application that the compressor, pump, or fan is used for, the reduction in flow and pressure may render the equipment inoperable.
RE: Electrical Motors - for use in India
In case of industrial application a 415V,50Hz (380V,60Hz) motor will solve the issue. If your equipments motors are for agricultural/similar field application then really you are gonna have a tough time ahead because, energy distribution for agricultural sector is not proper in India which lead to huge voltage fluctuations.
RE: Electrical Motors - for use in India
In case of industrial application a 400-415V,50Hz (460V,60Hz) motor will solve the issue. If your equipments motors are for agricultural/similar field application then really you are gonna have a tough time ahead because, energy distribution for agricultural sector is not proper in India which lead to huge voltage fluctuations.