do we need to exhaust air from wet well to meet NFPA 820 requirements or just supply outdoor air

do we need to exhaust air from wet well to meet NFPA 820 requirements or just supply outdoor air

do we need to exhaust air from wet well to meet NFPA 820 requirements or just supply outdoor air

(OP)
Do we need to supply and exhaust air to/from wet well at the rate of 12/30 air change to meet the requirement of NFPA 820 or just supply outdoor air.

RE: do we need to exhaust air from wet well to meet NFPA 820 requirements or just supply outdoor air

The purpose of the 12-30 ACH is to vent dangerous or explosive gases somewhere, so yeah you want to make sure the air goes somewhere.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources