Sizing of control power transformer fuses for degraded voltage conditions

Sizing of control power transformer fuses for degraded voltage conditions

Sizing of control power transformer fuses for degraded voltage conditions

(OP)
Hello,

Suppose in a plant that the voltage at an MCC is below normal due to a degraded switchyard voltage. Fed from the MCC are various motors which use size 1, 2 and 3 starters. With a degraded MCC voltage, the contactors are expected to draw more current due to a degraded source voltage. For 480/120V control power transformers, how can I verify that the fuse (primary or secondary) is sized such that it can tolerate such a condition? Generically, CPT primary or secondary fuses can be sized according to NEC or vendor recommendations, but may need to be sized larger in such cases. Thanks for your thoughts.

RE: Sizing of control power transformer fuses for degraded voltage conditions

Fuses should be sized to protect the transformer. If the existing fuses are failing, then larger fuses may result in control transformers failing. But go ahead. Remember, when you order larger replacement transformers, to specify control transformers with fuse holders and the appropriate size fuse pre-installed.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Sizing of control power transformer fuses for degraded voltage conditions

Are you serving motor load from the CPT? If not, how does the increased motor current at reduced voltage affect the CPT fuses? If you are serving motors from the CPT, then the fuses would be sized to carry motor starting current (which would be lower with reduced voltage) and should not be affected by a small increase in load current.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources