Transformer Vector Group
2

Transformer Vector Group

Transformer Vector Group

(OP)
We usually use Dyn11 transformers in distribution side.For one of new projects i got an offer from a company and in their technical specification the vector group was Dyn5.I understand that Dyn5 means a phase difference of 180 dgree.Is it possible to connect such a transformer to the existing grid..?

RE: Transformer Vector Group

(OP)
Thanks Steven i went through the post,still it is not clear for me whether i can use Dyn5 transformers in a grid using Dyn11 transformers.?

RE: Transformer Vector Group

By careful selection of which phase is connected to which terminal, you can wire it so that it functions as a Dyn11. Any Dy transformer can produce any of the Dy vector groups.

RE: Transformer Vector Group

(OP)
thanks ddavid..can u tel me how to rewire Dyn5 to obtain Dyn11 configuration..i mean 30 degree phase diff

RE: Transformer Vector Group

You do realize this is only an issue if transformers are paralleled, right?

RE: Transformer Vector Group

If the Dyn5 is connected X1-A, X2-B, and X3-C, then you can get to Dyn1 by connecting X1-B, X2-C, and X3-A. The you can use the referenced FAQ to get from Dyn1 to Dyn11.

RE: Transformer Vector Group

(OP)
Steven,connecting a transformer to supply implies paralleling it with other transformers ryt??Forgive me if its wrong,I'm a newbie.

RE: Transformer Vector Group

It is paralleled only if it is connected on both the high- and low-sides to other sources. If only the high side is connected to other sources but the low side is only connected to radial load with no other source of supply it is not in parallel.

RE: Transformer Vector Group

(OP)
Hv side is connected to 11Kv ring via Ring main unit and the LV side is connected to load..Im talking about a dedicated transformer used only for serving a particular district cooling plant equipments..

RE: Transformer Vector Group

Then no, it's not paralleled and the vector group is irrelevant.

RE: Transformer Vector Group

(OP)
so i can use a dyn5 transformer without any changes in the external connections..

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources