Joist hangers and end moments

Joist hangers and end moments

Joist hangers and end moments

(OP)
When you're designing a floor that has wood joists framing into other joists, do you consider the hangers transmitting moment? I have three 2x10 joists framing into a double 2x10 and it's failing in torsion when I consider the ends of the single joists as fixed, but it's obviously okay when I call it pinned.

How would you model this? Is moment really transferred?

Maybe I should just upgrade to a larger LVL beam to be sure?

RE: Joist hangers and end moments

Typical hangers (face mounted/top flange) are a pinned connection. They do not have the capacity to transfer moment. Typical wood joist construction should be modeled as pinned.

RE: Joist hangers and end moments

Joist hangers for timber floors are not intended to transmit moment.

RE: Joist hangers and end moments

Picture a cantilevered floor joist supported by nothing but a typical hanger at one end. You could tear it down with one hand....its pinned.

RE: Joist hangers and end moments

(OP)
Thanks. That's what I thought.

RE: Joist hangers and end moments

Depending on the connection to the purlin, a saddle hanger arrangement could transmit some moment across the beam, but I would not count on it. Just keep it simple...

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Joist hangers and end moments

Vote: pinned.

BUT you could use tie straps to get the beam to have top and bottom bracing at each joist to prevent LTB rotation. Stability bracing is not too hard to come by.

______________
MAP

RE: Joist hangers and end moments

I will also add (just to be picky) that depending on sizes/loading/span if you are only loading one side of a member then you may want to consider the effects of the applied torsion due to the eccentric load if the top of the 'one-side-loaded' member is not braced. Also you need to transfer the load to each ply.

EIT
www.HowToEngineer.com

RE: Joist hangers and end moments

How are you checking torsion in the double 2x10 anyway? If the joists actually transferred moment, the torsion in the beam would be self limiting as the joists would end up bracing the beam in torsion once they got done deflecting.

RE: Joist hangers and end moments

Excel is correct. This situation is only compatibility torsion, not equilibrium torsion. This is usually ignored in wood framing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources