Neutral ground resistor for mv generators
|
RE: Neutral ground resistor for mv generators
Yes it is typical and recommended for most utility generators. What you need to determine is fault current values (Phase to ground) that are acceptable for your system. As a rough rule of thumb, it is recommended that an ohm value be used in that the phase to ground current is around the phase to phase value during a fault.
If the system you are feeding is a high resistance grounded system that can run on a grounded phase, (as with critical process plants), the ohm value should permit a current to flow about that of the capacitive charging current (to ground) of the phase conductors.
RE: Neutral ground resistor for mv generators
What is confusing me is that there is no neutral. It is a delta connection.Any good technical articles to read on neutral ground resistor.
RE: Neutral ground resistor for mv generators
This is a brief short on standby generator grounding http://www.cumminspower.com/www/literature/technic...
If you are interested in neutral grounding resistors Post Glover has good products and resources. PDFS:
http://www.postglover.com/neutralground.html