FEMA 361 design loads

FEMA 361 design loads

FEMA 361 design loads

(OP)
I am looking at a small storm shelter within a larger building. I am designing per
FEMA 361. I am considering reinforced masonry for the walls. When designing the
MWFRS using ASD method, I know that I use .6W in all of the load combinations.
When designing the reinforcing in the walls for out of plane loading, can I use .6W
of the component & cladding wind pressure?

Also, if I go with reinforced concrete, using the strength method, I know that I replace
1.6W with 1.0W for all load combinations. Can I also use 1.0W with the C&C wind load
when designing for out of plane loading?

It seems to me that for extreme wind, the calculated C&C wind pressure is the ultimate
value, and does not get factored up for the strength method, and actually gets reduced for
the ASD method.

Am I interpreting this correctly?

RE: FEMA 361 design loads

I don't think so.

Quote:

I am looking at a small storm shelter within a larger building. I am designing per
FEMA 361.

FEMA 361 is a guide. ICC 500 is the new specification covering storm shelter design.

Quote:

When designing the MWFRS using ASD method, I know that I use .6W in all of the load combinations.

No - you use all required load combinatinos - that includes D+W and others. 0.6D+W is one of many that you need to check all designs with.

Quote:

When designing the reinforcing in the walls for out of plane loading, can I use .6W of the component & cladding wind pressure?

The use of MWFRS or C&C depends on what you are designing and the area of exposure of that element. For smaller wall segments you'd probably be using C&C wind
as the tributary area of a vertically spanning wall is H^2/3 where H is the wall height. For areas less than 700 s.f. you would use the C&C wind pressures.
Again - the load combinations ALL have to be checked, not just 0.6D+W.

Quote:

Also, if I go with reinforced concrete, using the strength method, I know that I replace 1.6W with 1.0W for all load combinations. Can I also use 1.0W with the C&C wind load when designing for out of plane loading?

If you use strength method - you would use the LRFD load combinations per the code. The use of a 1.6W assumes a strength design method. The use of 1.0W presumes the use of ASD design. These are independent of whether you are using C&C wind pressures or not.

Quote:

It seems to me that for extreme wind, the calculated C&C wind pressure is the ultimate value, and does not get factored up for the strength method, and actually gets reduced for the ASD method.
No - that is not correct. The wind pressure used is not related to the design method (strength vs. allowable).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources