modelling a PV invertor

modelling a PV invertor

modelling a PV invertor

(OP)
thread238-299994: Modeling a PV inverter for fault contribution into distribution system

I am working on a solar farm project wherein it is required to model the AC side of PV inverters connected to a 415V AC board through to the 11kv Grid through a transformer. (modelling of Solar PV modules are not required).In order to find the short circuit fault contribution,how can the inverters be modelled.

I am using SKM POwertools.

Can this be modelled as a Utility source or a Usual generator?
Hvae seen a previous thread related to this;however could nt find any conclusion in that.

RE: modelling a PV invertor

Do inverters for solar farms in your area require fault ride through?

RE: modelling a PV invertor

(OP)
No fault ride through is not a requirement. However, some of the large invertors comes with built-in FRT which conflicts with the requirement of Anti-Islanding protection.

RE: modelling a PV invertor

Hi, it is not necessary to make a model for inverter. According to the manufacturar the maximum short circuit current for inverter is 5 % more than the nominal current. Tiristor system inside of the inverter not allow current more than 5 %.

RE: modelling a PV invertor

As part of the UL listing process, the inverter manufacturer must measure AC fault current and duration. You should be able to get this information from them.
-JFPE

RE: modelling a PV invertor

I do know ASPEN has a model for a fault current limited generator, which is what I use.

Caution on modeling because if the units can generate reactive current, or are limited from producing reactive current will make a difference in the negative sequence part of the model. It will show up in the contribution into ground faults because of this. I haven't seen this with inverters, but I have seen this with DVAR systems.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources