Current Transformer Bandwidth

Current Transformer Bandwidth

Current Transformer Bandwidth

(OP)
Hey guys,

I was just wondering what to take into consideration when I am looking at the bandwidth perspective of choosing a CT.

RE: Current Transformer Bandwidth

How do you anticipate using it that you'd even be concerned about bandwidth?

RE: Current Transformer Bandwidth

To me this seems like it would be more of an issue with pulse or isolation transformers than current transformers. In any case, I would look up the concept of volt-seconds which impacts transformer saturation and ability to pass signal edges.

RE: Current Transformer Bandwidth

The core material can also important. Not sure on the details, but I know that some cores are better suited to unipolar pulses.

RE: Current Transformer Bandwidth

Since the OP hasn't told us the application, it's hard to say.

Just in case he's thinking of the motor side of a VFD, here's some prior work:

http://www.eng-tips.com/viewthread.cfm?qid=178369

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Current Transformer Bandwidth

(OP)
Sorry guys I got caught up with a lot of school work. I need to choose a CT that I can use to measure the THD up to the 51st harmonic of household appliances.

RE: Current Transformer Bandwidth

(OP)
I will be taking the measurements and will be inputting them into a DAQ, and will be displaying the THD in LabVIEW.

RE: Current Transformer Bandwidth

For standard power system CTs, response should be pretty good up through 50th harmonic. I looked into this several years ago. There are some seminal IEEE papers by D.A. Douglass that cover frequency response of CT and PTs.

RE: Current Transformer Bandwidth

It's something that should be very easy to test / measure using simple test equipment. Then, one should be able to calibrate out any response curve. This is assuming that the CT doesn't go totally 'deaf' at such low kHz (seems unlikely).

Good luck.

RE: Current Transformer Bandwidth

I think you are going to face bigger challenges than the CT. What level of attenuation are you looking at with the 51st harmonic? In other words, will you have enough signal to measure with your equipment? Will interference from other sources like you power supply be problematic? I assume you are planning on using an FFT for this, do you have a sufficient number of clean samples to get sufficient bin resolution? Things like that become real problems in physical applications that aren't apparent in simulations.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources