Hi,

I have a bus which has a 25kA/1sec fault rating. Is this normally compared to IEC 60909-0 sub-transient, transient or steady state fault level? Any help is appreciated.

RE: Bus 1sec fault rating vs IEC 60909-0

IEC 60909 it is a method how to calculate the short-circuit currents, indeed, but you have to calculate these currents according to your actual network configuration-involved impedances and source voltages. The bus bar rating you can appreciate according IEC 60865 "Short-circuit currents - Calculation of effects".

RE: Bus 1sec fault rating vs IEC 60909-0

(OP)
My question is for the generators in my network, which impedance (sub-transient, transient or synchronous) is used when trying to establish if the 25kA/1sec fault rated bus is adequately rated.

RE: Bus 1sec fault rating vs IEC 60909-0

bdfig,
It should always be sutransient to get the maximum symmetrical short circuit current at the location to compare with bus rating.

RE: Bus 1sec fault rating vs IEC 60909-0

(OP)
Hi Kiribanda,

Is there a standard (preferably IEC or AS) which specifies this? I certainly support this approach(especially since the switchboard does not have a shorter time rating). However I have been getting some pushback saying this is overly conservative, and would like something concrete to point to.

RE: Bus 1sec fault rating vs IEC 60909-0

I think IEC 61439 is likely the place to start. I'm not at work right now so I can't check the exact wording in the standard, however there is some discussion in section 8 of http://www05.abb.com/global/scot/scot209.nsf/verit... which does make note of special conditions close to generators.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources