Natural Gas Pipe Sizing
Natural Gas Pipe Sizing
(OP)
Hi,
Does anyone know whether the hybrid pressure method for gas pipe sizing as described in ANSI Z223.1-127, can be used for pressures above 2 psi upstream of the regulators?
Thanks a million.
Does anyone know whether the hybrid pressure method for gas pipe sizing as described in ANSI Z223.1-127, can be used for pressures above 2 psi upstream of the regulators?
Thanks a million.





RE: Natural Gas Pipe Sizing
This method, which splits the system into distinct pressure regions, can be used regardless of the pressures in the piping, either upstream or downstream of the regulator.
If using tables, be careful to stay within the pressure drop constraints listed for the tables. But, be careful, even to do that.
I generally do not use the tables, since sometimes the above constraints list pressure drops in excess of 40% of the inlet pressures and the equations used to generate the tables are typically constrained to no more than 20%. So I would question any table that exceeded 20%.
RE: Natural Gas Pipe Sizing
I use the equations rather than the tables which as you mentioned are limitting.