Paralleling generator with autotransformer
We are attempting to connect a temporary generator in a standby application. Site is equipped with 3x 1100 kw, 600V diesel generators which parallel using woodward 2301A LSSC, and Cat VR3 regulators utilizing droop. Generator pitch is .8.
One unit is off line for repair--in its place we connected a 1250 kw unit, pitch .7333, Cat VR6. I know that dissimilar generator pitch is not desirable, however a small amount of circulating current is acceptable in this temporary application. Temporary generator voltage is 480 which is stepped up to 600 using an autotransformer. Generator neutrals are solidly connected. Neutral to ground bond was removed from temporary unit. Load gain, frequency, voltage and voltage droop were adjusted to match existing units.
Temporary was closed to bus and approx 1000 kw of 600V resistive load applied (approx 1000A). We then synched one of the existing units to the bus and the temporary 600v breaker kept tripping on ground fault at the moment of syncronization, presumably due to circulating current on the neutral. Was told by a couple sources that an autotransformer is not desirable for this application. Upon a recommendation, the generator neutral was disconnected from transformer X0.
Above sequence was replayed, and breaker no longer tripped. Temporary and existing shared kw in proportion, power factors were approx. .96 lead and .95 lag indicating that voltage droop settings were close to being satisfactory. Other existing unit was closed to bus and this is where things went badly. Current on temporary increased to 1000A, existing were carrying approx 500A each, suggesting 1000A of circulating current. Voltage dropped to 550V. We opened breaker on last existing unit and readings returned to same as before. All existing units synchronized and shared kw and kvars very well before connection of the temporary.
Any comments on the autotransformer or any other suggestions?
RE: Paralleling generator with autotransformer
Check the voltage on the last incoming unit. Check your cross current compensation CTs for polarity and loose connections. Check your single/parallel switches for opens.
Before disconnecting the neutral connection I would try to decrease the sensitivity of the ground fault tripping unit.
Bill
"Why not the best?"
Jimmy Carter
Waross, voltage of the last unit was checked and matches that of other units. We paralleled the two existing units with no problem. Using voltage droop, not cross current compensation so there are no single/parallel switches. Voltage droop operation of temporary was verified ok. We actually did have to reverse the CT polarity in order to get it functioning. Ground fault sensitivity was set to max to no avail.
Are you taking your voltage sensing from the auto-transformer wye point or line to line? I would suggest trying line to line for sense and power to the AVR. With the different pitches you may be getting weird distorted wave forms on the neutral of the auto-transformer. Circulating current is often reactive and voltage differences between generators or transformers cause reactive currents.
Bill
"Why not the best?"
Jimmy Carter
AVR sensing and power is L-L on the 480V side.
Quote (IBRCAN)
You may want to re-check this. You have the symptoms of a compensation circuit increasing the voltage when it should be reducing it.
Bill
"Why not the best?"
Jimmy Carter