Determine the correct setting for Under Frequency Relay (UFR) for Generator

Determine the correct setting for Under Frequency Relay (UFR) for Generator

Determine the correct setting for Under Frequency Relay (UFR) for Generator

(OP)
Dear all,
We operate four generators in our steam power plant. 2 X 100 MW and 2 X 200 MW. They are Toshiba Generator. Built in 1980 and 1987. Our Grid Frequency is 50 Hz. According to Our National Grid Code, our generator must continuous supply the grid in the frequency range of 47,5 - 52 Hz. But, based on our equipment operation manual (published by Toshiba), it was stated that the permissible continuous operating range is 48,5 - 50, 5 Hz. This is done to reduce the possibility of damage due to High Cycle Fatigue. My question is,
1. Could you recommend us the correct setting for Our Under Frequency Relay (UFR) based on the condition mentioned above?
2. Could you give us explanation about the natural frequency of the steam turbine?
..Thanks a lot.

RE: Determine the correct setting for Under Frequency Relay (UFR) for Generator

Does your Grid Code allow exceptions for machine limitations?

RE: Determine the correct setting for Under Frequency Relay (UFR) for Generator

I suspect the Toshiba requirements are for continuous operation. A momentary excursion below or above this should not be an issue. But I'd set the UF to pickup below the 48.5 Hz with a inverse time function if possible. Or two levels of UF with different time delays. Basically, I'd set the relays to protect the machine and let someone higher up argue with the Grid Authority - unless they plan to buy you a new turbine-generator when this one fails.

Natural turbine frequencies are resonant frequencies of the mechanical system where vibration issues can get amplified. Basically, you should not operate at a critical frequency - you need to accelerate through the critical frequency and don't linger.

dpc

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources