thread238-82004: Sizing personal protective grounds on a 15kV distribution system
Does anyone have a clear method to size temporary protective grounds? I have read IEEE 1246 and that doesn't seem to go into enough detail. I have read IEEE 1048 and it references some tables in ASTM F855-1997. However I can only get access to ASTM F855-2009 which doesn't seem to have the tables anymore. ASTM F855-2009 has Table 1 for X/R ratios of 1.8 or less and Table 2 for X/R ratios of greater than 1.8 however I can't understand how to use table 2, it doesn't seem to give enough information. Any help or guidance would be appreciated.

RE: Sizing Temporary Protective Grounds

Check out Chance Section 3000 (Grounding Equipment) http://www.hubbellpowersystems.com/literature/ency... . We size our grounds for the breaker failure clearing time. A few locations require 2 sets of grounds due to high fault current or slow clearing times, which is clearly posted with signs at the grounding locations. The portable grounds should be a short as possible.

RE: Sizing Temporary Protective Grounds

I went through this quite a while back but have no idea where I stuffed all the documents I referenced and the calculations for it. Check out the appendixes and references listed in the USBR grounding document as it might help you get going. http://www.usbr.gov/power/data/fist/fist5_1/vol5_1...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources