Limiting Oxygen Concentration for an Isomerate Storage Tank
I am looking for a basis for LOC (same as Minimum Oxygen Concentration) when applying nitrogen purge to an Isomerate storage tank. Can anyone explain to me the tactics in developing this? I understand it is based on LEL and have seen variance based on pressure, altitude, etc.... Can someone help me gain a little better understanding of this? As well i understand a common practiced safety factor is 25% of the LEL.
RE: Limiting Oxygen Concentration for an Isomerate Storage Tank
thread135-15647: Nitrogen Purge Rates For "Atmospheric" Vessels
thread135-115960: flammability limits (fire)
thread124-53646: Nitrogen Purity - Is 98 % too low?
thread798-255535: Blanketing
thread798-33615: How to Calculate Flammability of gas mixture
thread798-144582: Limiting Oxygen Concentration
thread816-162978: Flash Back Protection (LEL/LFL determination)
Good luck,
Latexman
C3H8 + 5O2 ----> 3CO2 + 4H2O
LFL C3H8 = 2.2% in air
LOC = 2.2 x 5 = 11.0% (11.5% by lab data)
Good luck,
Latexman
Latexman is right.
The logic of such an estimation is given by:
LOC = [moles Fuel/(moles Fuel+moles Air)](moles O2/moles Fuel)
= LFL (moles O2/moles Fuel)
Idk how applicable this is but just for simplicity I took to basic hydrocarbons Methane and Propane
C3H8 + CH4 + 10 02 -----> 2 CO2 + 6 H20
In this scenario your multiplier would be 10
So LOC = LEL of this compound x 10 ??
Good luck,
Latexman
As stated by 25362 LEL= (moles of O2/moles of fuel) so in terms of propane its LEL = (5 moles of O2/ ????) where do you determine the moles of fuel being that wouldnt it just be one mole of fule sorry my chemistry has left my brain at the moment.
Good luck,
Latexman
Good luck,
Latexman
Good luck,
Latexman
Stoichiometry.
In regards to LEL once i have determined LELs for all of the chemicals in Isomerate would I then use Le Chatelier's mixing rule? LEL(Mix)=1/(Sum(xi/LELi))
C7H16 + 11 O2 = 7 CO2 + 8 H2O
Air = 11/ 0.21 = 52.38 moles air /mole of C7H16 at stoichiometric conditions
Could either of you explain the stoicometry used to develop the LEL from this equation. This will provide with a good example which I could use to approach the other chemicals.
Good luck,
Latexman
From the book by Crowl and Louvar, Chemical Process Safety: Fundamentals with Applications - Prentice Hall, the flammability limits for many hydrocarbons could be roughly estimated (although experimental determinations are always recommended) using the following equations:
LFL = 0.55 Cst and UFL = 3.50 Cst; where Cst is volume % of fuel in fuel plus air.
Combustion stoichiometry shows:
where z = m + x/4 - y/2.
z is moles O2/mole fuel. The result is then:
In your example:
m =7; x = 16; y = 0
LFL = 55÷(4.76×7 + 1.19×16 +1) = 1.03 vs actual 1.1%
UFL = 350÷(4.76×7 + 1.19×16 +1) = 6.6 vs 6.7% actual.
Refer to thread798-33615: How to Calculate Flammability of gas mixture.
I've seen plants using 40% of the MOC and even less with ketones.
NE = S { NEi * I%i }
where I%i = fractional quantity of ith Inert component
NEi = nitrogen equivalent of ith Inert component
CLF = Sigma { F%n } / Sigma { F%n / CLn } = low limit of Flammable portion in Air
CLM = Sigma { I%i + F%n } / Sigma { F%n / CLn } = low limit conc of total Mixture in Air
where F%n = fractional quantity of nth Flammable component
CLn = lower limit of nth Flammable component
How do they differ and which is preferred?
Finally so essentially applying a safety factor of 40% would equate to (LOC-(LOCx.4))
My intention was ≤0.4 LOC.
Good luck,
Latexman
In addition.
The same book by Crowl & Louvar gives an example of how to estimate the LFL and HFL of a mixture of air with flammable gases, based on Le Chatelier's empirically derived equation to determine if a certain mixture is flammable or not.
yi = mol fraction of the flammable gas i in the mixture with air
LFLi = LFL of the flammable gas i in the mixture
UFLi = UFL of the flammable gas i in the mixture
The authors advise us that empirical formulas like these have their limitations. Therefore, I suggest following Latexman's advice.
BTW, the lowest (roughly) estimated LOC doesn't necessarily go with the lowest LFL. Take, for example:
Metane: LFL = 5.0. LOC = 5.0×2 = 10.0
Hexane: LFL = 1.1. LOC = 1.1×9.5 = 10.45
Ethylene: LFL = 2.7. LOC = 2.7 ×3 = 8.1
Heptane: LFL = 1.1. LOC = 1.1× 11 = 12.1
Acetone: LFL = 2.5. LOC = 2.5×4 = 10.0
http://d.yimg.com/kq/groups/3862917/197829902/name...
http://www.fire.tc.faa.gov/pdf/TG3.pdf
www.airproducts.com/~/media/downloads/article/N/en...