Plate & Frame Hex hot vs cold sides differential pressure

Plate & Frame Hex hot vs cold sides differential pressure

Plate & Frame Hex hot vs cold sides differential pressure

(OP)
Good day,

We have a problem with a crude oil cooler.

The oil comes from a high (80ºC) process at a relatively low viscosity (1.38cP). It is cooled down by water to about 40ºC, where the viscosity increases to about 7.33cP.

The problem is that, as the viscosity increases the differential pressure between the hot oil and cold water sides varies throughout the unit. Plate and frame, usually, allow for up to 6kPa pressure differential, which is very minimal.

We have busted couple plates.

In theory, the pressure drop throughout the unit should remain constant and minimal, but apparently it isn't.

Has anybody experienced similar problems to this scenario?

Cheers!

<<A good friend will bail you out of jail, but a true friend
will be sitting beside you saying ” Damn that was fun!” - Unknown>>

RE: Plate & Frame Hex hot vs cold sides differential pressure

This type exchanger has small flow passages, which can be easily fouled or filled with debris if the process fluid (crude oil) is not clean. have the failed plates failed due to debris or fouling?

investigate/inquire with the mfg about maximum or allowable DP across the exchanger. there ought to be a data sheet for subject exchanger and if available, i recommend reviewing the data.

hope this helps.
-pmover

RE: Plate & Frame Hex hot vs cold sides differential pressure

6kPa DP between sides on a PHE is very small, we have industrial units from Alfa Laval running hundreds of kpA delta. This doesn't help you a lot but I'm surprised at the comment "usually allow up to 6kPa differential".

Are your units correct?

As a chem eng/metallurgist the first part of any answer I give starts with "It Depends"

RE: Plate & Frame Hex hot vs cold sides differential pressure

7 cP also doesn't seem that high of a viscosity to stop flow. The skin temperature of the oil would be lower but not enough that I would suspect a problem. Do you have any idea of the pour point of the oil?

RE: Plate & Frame Hex hot vs cold sides differential pressure

(OP)
Just got back from site.

I verified and the mfgr specs are 6kPa differential on the sides.

Looking at the damage, yes it was caused by the bending of the plates due to the differential in pressures.

Apparently one exchanger was damaged when the oil got thick enough that the pressure drop was significant (the oil is cooled with the glycol) at the end plates (out for oil). The other was busted when they connected a pressure truck to flush it.

These are the less expensive and smaller footprint exchangers available. I guess it is time to look for other options..

Thanks for your replies

<<A good friend will bail you out of jail, but a true friend
will be sitting beside you saying ” Damn that was fun!” - Unknown>>

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources