A/C replacement for a load out room

A/C replacement for a load out room

A/C replacement for a load out room

(OP)
Currently trying to do an approximate estimate of the tonnage needed to cool a smaller room containing several transformers.
Theres nine trans. ranging from 30 kva to 1250kva. This is the first time looking into it and i've yet to find a way to calculate the heat in watts.

The previous system was a 10 tonne system, but using an approximation from engineering toolbox, the system would be giving off about 33 tonnes.

EX: 1250kva * 20 = 25000 watts of heat...

Anyone point me to some reading where I can varify the approximation or any help at all!

RE: A/C replacement for a load out room

1) Ask the manufacturer of the transformer is always best.
2) Look up some tables in ASHRAE or other reputable publication to get an approximate value

RE: A/C replacement for a load out room

I multiply transformer kVA by inefficiency (3-5%), thats the load in the space, then multiply by 3.4 to convert to Btu.

Thats your SENSIBLE load to meet.

1250 kVA * .03 * 3.4 = 127 MBH = 10 tons of cooling

knowledge is power

RE: A/C replacement for a load out room

maybe they used diversity?

knowledge is power

RE: A/C replacement for a load out room

I have used 2% of projected load (and perhaps some margin) as the loss for a lot of transformers, but the inefficiency must come from the manufacturer. If you use the nameplate capacity you quickly get monster oversize. Electrical engineers do not size transformers near the duty point like you do with chillers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources