Currently trying to do an approximate estimate of the tonnage needed to cool a smaller room containing several transformers.
Theres nine trans. ranging from 30 kva to 1250kva. This is the first time looking into it and i've yet to find a way to calculate the heat in watts.
The previous system was a 10 tonne system, but using an approximation from engineering toolbox, the system would be giving off about 33 tonnes.
EX: 1250kva * 20 = 25000 watts of heat...
Anyone point me to some reading where I can varify the approximation or any help at all!
Theres nine trans. ranging from 30 kva to 1250kva. This is the first time looking into it and i've yet to find a way to calculate the heat in watts.
The previous system was a 10 tonne system, but using an approximation from engineering toolbox, the system would be giving off about 33 tonnes.
EX: 1250kva * 20 = 25000 watts of heat...
Anyone point me to some reading where I can varify the approximation or any help at all!





RE: A/C replacement for a load out room
2) Look up some tables in ASHRAE or other reputable publication to get an approximate value
RE: A/C replacement for a load out room
Thats your SENSIBLE load to meet.
1250 kVA * .03 * 3.4 = 127 MBH = 10 tons of cooling
knowledge is power
RE: A/C replacement for a load out room
knowledge is power