Partial Snow Loads
Partial Snow Loads
Hi all, I have been trying to find out a good way to design a steel roof system in RAM for snow loads for some time.
Problem:
RAM treats snow loads as live loads, and creates a "worst case" scenario by "skip loading" - applying all or nothing on cantilevers/backspans. However, according to ASCE 7, balanced snow loading only needs to be staggered 50%/100% (the section on partial loading for multiple spans). This results in RAM being overly conservative (by 20% in a simple test structure).
Solution attempt:
I am assigned to try to come up with a reasonable workaround, but so far I don't think there is a reasonable solution. Does anyone know whether any of the live loads (storage, partitions, etc) are NOT staggered? If so, I can apply this load as a uniform load equal to one half the snow load, effectively causing RAM to stagger my snow loads 50%/100%. I cannot use a dead load for this due to deflection criteria.
I hope RAM isn't completely worthless for snow loads...
- Aaron
Problem:
Solution attempt:
- Aaron
RE: Partial Snow Loads
If you make all of the framing lateral and process the designs in Ram Frame, you have more control over the load combinations, but you still won't get deflection checks going that route.
Other than the dead load trick you might have to do some manual checks by superimposing the moment demands from the live load patterns.
Deflection and ponding coupled with clogged roof drains may be a more important design criteria to consider.
Steve
In reality it isn't this high. A few girders are deflection controlled, and a few are controlled by minimum flange width. Still, I'd like to save a few tons of steel if possible. Anyway, my boss wants to figure out if RAM is worth using in the future, and to compare RAM sizes with RISA sizes. We would rather not specify 10% more steel than already required - after all, the snow load is a rare event, there is a huge load factor, material strengths are very conservative (available bending strength doesn't account for Ry or strain hardening), our dead loads are conservative, etc. Why add in extra conservatism?
All in all, it seems this dead load workaround is good in this case, but not in cases where live load deflection might govern.