Has anyone experienced the following:

In a "island" type facility, power is supplied from three (3) 12.47kV generators in the moment we close the breaker of the first gen set against the "dead bus" we getting overvoltage reading of 25,000 volts for a few cycles. this value was maesured with some test isntrumentation ( & Easy power ). Problem came to evidence when the fuse ( at 480V bus )that serves the elevator started to blow. After reviewing everything related to the elevator is was pretty clear that the problem was elsewhere. Once it was determined that everytime we started the plant gensets we proceeded with the measurements that showed that overvoltage condition.

If the gen-set is OK, what can be the cause for this

RE: Generator Overvoltage

It could be ringing due to a capacitor bank being energized or distributed capacitance of the cabling system.

Do you have a way to determine the frequency of the voltage spike?  

I'm assuming the generator voltage is nominal before you close the breaker?   

RE: Generator Overvoltage

(OP)
Voltage was nominal, I was thinking that the cable distribution ( Impedance) might be the culprit. I will try to see if the charts have the frequency not one 100% sure. Do you know of any mitigation systems

RE: Generator Overvoltage

How much of the system are you trying to energise in one go?

Is it possible to connect the first generator to the main bus and then re-energise parts of the system after that?

RE: Generator Overvoltage


It may be possible that a 'ferroresonant' condition occurred.  Recently discussed at: Thread238-33645
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources