Dranetz PX5 Metering Question

Dranetz PX5 Metering Question

Dranetz PX5 Metering Question

(OP)
I have a customer that I am performing a load survey for. The purpose of this survey is to see how much current a three phase 400A feeder is drawing for one week. My customer would like to add load to this particular feeder. I received the data and noticed the min, max, and average data are very different. There are a lot of motor loads in this circuit. I realize there is going to be inrush current for each motor. Is the average RMS current the actual value I should use in my report? The average current was Approx. 180A and Max Current was 356A.

RE: Dranetz PX5 Metering Question

None of the above, what you need is the 15 minute demand current.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources