IRC 2009 Live Load Reduction Formula
Does the IRC have a live load reduction formula like IBC. Thanks
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
IRC 2009 Live Load Reduction FormulaIRC 2009 Live Load Reduction Formula(OP)
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
RE: IRC 2009 Live Load Reduction Formula
Highly unlikely, depending on the framing, that any single family residence structure would gain the provision though.
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
The 2006 IRC has a table (R301.6) for pitch reduction that allows a 16 psf live load for 4:12 to less than 12:12 pitches. It also has a table (R301.7) for area reduction that is close to the 2006 IBC.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
The OP's question was with regards to live load and you are referring to roof live load. They are not one and the same. Also, table R301.7 is for allowable deflection of structural members. No where it talks about any reduction is live load, unless I am missing something. I am looking at IRC2009...don't have IRC2006.
Mike McCann
MMC Engineering
The OP also is referring to the 2009 IRC (which I do not have a copy of here) not the 2006 IRC.
It also refers to live loads not floor live loads. Which are in the 2006 IBC both under the Live Load (section 1607 of the 2006 IBC) so how is one to assume that only floor live loads are referred to in the OP? The 2006 IRC also refers to roof loads as live loads, see section R301.6.