For those who have more experience than my in the HVAC world:
When I do building inspections,I sometimes see EER or SEER energy efficiency ratings on rooftop Heat Recovery Ventilators or RTU's. Othertimes, I don't. Same with the plans. Sometimes they are listed and sometimes they aren't.
The recent building I did was a school, and there were EER ratings for all of the rooftop equipment except for the HRV's that served the restrooms. These were plate heat exchanger HRVs. The other HRVs all had energy efficiency ratings.
Any ideas as to why?
When I do building inspections,I sometimes see EER or SEER energy efficiency ratings on rooftop Heat Recovery Ventilators or RTU's. Othertimes, I don't. Same with the plans. Sometimes they are listed and sometimes they aren't.
The recent building I did was a school, and there were EER ratings for all of the rooftop equipment except for the HRV's that served the restrooms. These were plate heat exchanger HRVs. The other HRVs all had energy efficiency ratings.
Any ideas as to why?





RE: Energy Efficiency Ratings for HRV sometimes not shown
Somebody else may have a better memory than I, so don't take my answer as definitive. I could (and frequently am) wrong.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
RE: Energy Efficiency Ratings for HRV sometimes not shown
>>These fora should not be used to bypass your own in-depth research on the issues that affect you, nor is it intended to be >>a substitute for appropriate professional assistance within your field or geographical region.
RE: Energy Efficiency Ratings for HRV sometimes not shown
RE: Energy Efficiency Ratings for HRV sometimes not shown
However, I think you missed the terms EER and SEER in the original post. Delta enthalpy is the effectiveness, EER is the efficiency. EER and SEER are related to the heat recovered by the ventilator divided by the electric energy input for the driving motor, auxiiaries, and controls.
Thus, no standard requirement = no need to mark it on the unit or spec sheet. If you see them marked anyway, the purpose is for marketing.
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
RE: Energy Efficiency Ratings for HRV sometimes not shown
alternatively if you can decipher manufacturer and model# you can get that information from the manufacturer. Keep in mind for ERV efficiency depends on flowrate.