I am working on a project where the architect wants to "nail" five 10x10 timber columns together to create a large, wide column element. The AITC manual does not provide any criteria for the spacing of spikes other than to not split the wood and information about the drill size for pilot holes. I am specifying 1/2" diameter spikes at 6" o.c. with the spikes in each "layer" staggered 3". Just curious if anyone has any rules of thumb picked up in the timber framing world that might be helpful. Thanks.

RE: Spacing of spikes

What the hell are you building???

How about drilling through and using bolts or All_Threads??

RE: Spacing of spikes

Never heard of doing this - usually just thru-bolted. I would think with 7/16" pilot holes at the 3" spacing though you should be OK. Just watch the edge distances.

I guess I would have to ask if he just wants to see a spike for the Architectural effect? If so, just pound the exposed boltheads to smitherines! hammer

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Spacing of spikes

(OP)
The architect wants a column 46 1/4" (five 10x10's side by side) x 9 1/4". Could thru-bolt, but the architect does not want to see the bolts/nuts. There are no edge distance criteria for spikes/nails like there is for bolts, unless you just use the same criteria which is what I intend to do.

RE: Spacing of spikes

You can always cap in the bolts and plug the ends with wood dowels. Like the spike heads won't show!

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com

RE: Spacing of spikes

glulam?

RE: Spacing of spikes

(OP)
Not looking for options. Glulam is not an option. The architect wants the spike heads to show. Go figger, but this is what the architect convinced the owner to do. I'll just use the same edge spacing and fastener spacing criteria as for a bolt.

RE: Spacing of spikes

Dry environment, I hope... I would probably 'tack' them together with pre-drilled spikes and use adhesive... Shrinkage could be a whole bunch... and likely develop face splits... 5 - 10x10's would have a load capacity of maybe 500K... how tall is the building <G>...

Dik

RE: Spacing of spikes

I would thru bolt the center three 10x10's with counter sunk nuts. Then spike the end 10x10's for the look.

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.

RE: Spacing of spikes

use the glulamm and nail the 2x10 on the exterior

RE: Spacing of spikes

search "loghog" from fastenmaster

______________
MAP

RE: Spacing of spikes

I like the combo option from Boo and Woodman by facing a large glulam with non-load-carrying lumber by spiking them to the engineered column. The thru-bolts being counter sunk is perfect too.

Before you doing anything creative, make sure the code likes the artwork you are trying to wow the world with.

RE: Spacing of spikes

Look at timber bridge deck details. We have built some decks using 12x12's and using sledge hammers to install the spikes. I'm not in my office now - but I remember some timber bridge drawing details with a blue cover(!). I used an oval platform constructed like this for a tunnel work platform on a 40 degree slope. I believe these details are quite common.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close