IR test for Heat Trace Cable
IR test for Heat Trace Cable
(OP)
Looking for acceptable values for IR results for heat trace cable. One manufacturer indiactes a minimum reading of 20 megohm is acceptable. That seems low.
Thanks.
b
Thanks.
b






RE: IR test for Heat Trace Cable
http://sas.ieee.ca/pesias/seminar_slides/PES-IAS%2...
RE: IR test for Heat Trace Cable
http://www.thermon.com/catalog/us_pdf_files/pn5020...
"IEEE 515 recommends that the test voltage for polymer insulated heating cables be 2500 Vdc. Minimum resistance should be 20 megohms."
RE: IR test for Heat Trace Cable