Meggering of LV Busbar

Meggering of LV Busbar

Meggering of LV Busbar

(OP)
Hi all

May i ask is it necessary to do a megger test on a 400V MCC busbar for a shutdown maintenance? I have limited manpower and time, thus i would like to give this item a miss. Please advise if there is any standards that recommends maintenance for LV switchgear? Thanks!

RE: Meggering of LV Busbar

Not necessary. You get a lot more from IR inspection while it is energized. Then you know where to work when you are down.

RE: Meggering of LV Busbar

If you deenergise a swbd for maintenance in the area other then horiz and bus bar chambers then there is no need to do a megger test on the busbars prior to re energisation.

You should however megger any circuits /compartments in which you did do any maint work prior to switching those on.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources