riser sizing

riser sizing

riser sizing

(OP)
Sorry for asking such a basic question!
In a 6 floor car parking the design area consists of 12 sprinklers in 6th floor.Suppose the flow rate to be 240 g.p.m and the feed main pipe size to be 3".What will the flow rate for which the riser size will be calculated at lower floors?The same 240 g.p.m or more? Not a combined system,wet sprinkler ,similar floors.


RE: riser sizing

You can just calc the worst case area (assumed as the 6th floor in your case) and size the others based on that. So, whatever pipe sizing you have for the 6th floor, that would be replicated on the 1-5 as well.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

RE: riser sizing

(OP)
Thank you TravisMack for your reply . By "riser" I mean the vertical pipe feeding floor main pipes.So my question is : What is the size of this vertical pipe between floors ? Will the size be increased in lower floors or not and if it will,how much; proportional to number of design area sprinklers in every floor or any other way?
best regards

RE: riser sizing

I understand the vertical pipe between floors is what you are talking about. You will size it based on calculations on your worst case area.

You can have a 4" riser feeding a 10 story office without issue, if you have enough pressure. I assume you are not sizing per pipe schedule and are sizing per hydraulic calculations. If the latter, then the calcs drive the size. If you need bigger pipe closer to the bottom to help with friction loss, then so be it, but it is soley determined by calculations.

Travis Mack
MFP Design, LLC
www.mfpdesign.com

RE: riser sizing

(OP)
Travis Mack
It is the latter.Thank you very much.You are very helpful .

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources