Why Fire Hose Cabinets in Small Buildings?

Why Fire Hose Cabinets in Small Buildings?

Why Fire Hose Cabinets in Small Buildings?

(OP)
As per IBC, the Standpipe is required in any building only if the floor level of the highest floor is more than 9.14m from lowest level of fire department vehicle access. That means that if a building is 3 storey with 4m for each storey, the floor level of highest storey will be 8m and according to IBC Fire hose cabinet is not required. I have seen many projects where such buildings are provided with FHC's. Can anyone help in explaining this?

RE: Why Fire Hose Cabinets in Small Buildings?

If you do not know the code , you cannot enforce it properly

Are most of these buildings sprinkled???

May be someone specifying it, even though not required

RE: Why Fire Hose Cabinets in Small Buildings?

CDA is correct. I continue to review designs for fire protection is specified that is not needed. For example, I have about dozen 4-6 story apartment buildings where the fire alarm contractors will install manual pull stations throughout the buildings. Manual pull stations have not been required for over 3 years in buildings protected by either NFPA 13 or 13R sprinkler systems that activate occupant notification devices. In three of these buildings a fire protection engineer has prepared the designs and no pull stations. Some owners are paying $60-70K for pull stations, wiring and contractors they could spend on something else.

RE: Why Fire Hose Cabinets in Small Buildings?

(OP)
cdafd, Yes these buildings are sprinkled.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources